Building a House - I Want to Wire for Flair

Answered

Comments

8 comments

  • Official comment
    Avatar
    Daniel Myers

    Hi James,

    Thanks for reaching out and sorry we didn't make this easier - I went ahead and updated the article to include a link to this transformer.
    In terms of wiring, they can be daisy chained or wired in parallel.  I also was speaking with our engineers last week and they have suggested that 15 vents off of this transformer is perfectly fine as well rather than the listed 10 vents in the included instructions - I also updated this on our knowledge base as well.

    Hope that helps and please do reach out either here or directly to our support team if you have any additional questions!

    Cheers,
    Dan 

    Comment actions Permalink
  • Avatar
    James Hamersbach

    Thanks!  That clears that up nicely!

    1
    Comment actions Permalink
  • Avatar
    Daniel Myers

    Brian Wuttke - I believe it's possible to tell that the vents are hardwired by the voltage reported - asking engineering.  We aren't currently doing anything different for wired vs battery powered vents.

    Jim - we recommend this transformer and I think whether its wired in parallel or series doesn't end up mattering so wire nuts or a terminal block might be your best set of options.  Happy to clarify further if it would be helpful!

    1
    Comment actions Permalink
  • Avatar
    Daniel Myers

    @Brian - Engineering says that most likely it is detectable implicitly via the system voltage.  We'll consider upping the polling speed among other things - I filed a ticket internally to track it and I know there are some similar changes for non-gateway pucks that are wired so it could be cool to roll those out together.  Thanks for the suggestion.

    Cheers,

    Dan

    1
    Comment actions Permalink
  • Avatar
    Brian Wuttke

    Daniel Myers Do the vents know they are hard wired? I have 4 (so far) out of my 14 vents hard wired with 18/2.  Do the vents operate differently being hard wired rather than battery?

    0
    Comment actions Permalink
  • Avatar
    Jim

    James, did you get this wired and was that the transformer you used? I had the exact same issue looking at transformers. Did you just connect all the 20AWG wires together or something? Thanks!

    0
    Comment actions Permalink
  • Avatar
    Brian Wuttke

    @daniel and @jim they should be wired in parallel. They have minimal load so you can daisy chain a bunch of them together on an 18/2 LVT wire.

    @daniel you should change the programming of the hard wire vents so they operate without needing any power saving programming.

    0
    Comment actions Permalink
  • Avatar
    Jim

    Thank you Brian Wuttke and Daniel Myers - that’s helpful. Looking forward to this system in my new home.