I've set my thermostat to have the fan to "circulate," which means the fan should run 33% of the time. I've also enabled :Enhanced Circulation" in Flair. However, the fan never runs to circulate the air. Is there a step that I'm missing?
-
Official comment
Hi Dean Woodbeck,
I looked at your Flair home and noted that the Set Point Controller (aka SPC) option for your Flair home is set to "Flair app".
When you use the SPC = Flair app setting, Flair is in control of the set points and modes on your Honeywell thermostat.
The likely issue here is that Flair is putting your Honeywell into a mode that prevents the fan cycles from running.
If you are not using the SPC = Flair app option for a very specific reason, you could switch this to SPC = Thermostat. Using SPC = Thermostat would allow your Honeywell to be in charge of the modes and set points, and Flair would focus solely on the task of redirecting the airflow as needed.
Give this a shot, and if this doesn't solve your issue, please reach out to our support team for further assistance - support@flair.co
Regards,
The Flair Team